Batrium Critical Fault - How to identify?
slimf
Hi
Today my batrium keeps tripping my breaker - and I am trying to work out why. This is the log I extracted. It shows 3 critical faults, but I am attempting to determine exactly what the fault is!
Does someone know how to read this log? I cant work it out.
Note: I noticed Ambient Temp is -40 (and I can assure you its not) - However I don't have any low ambient settings enabled - So regardless it shouldn't cause a critical fault. Can someone advise if this is normal on a WM5? Ive never noticed it before, but then again never really took any notice of it.
System 4795 - SYS4795
Tower of Power
TimeStamp 14/11/2021 3:06:31 PM
System status information
Device Time Startup Ambient Supply
14/11/2021 3:06:38 PM 14/11/2021 1:35:37 PM -40ºC 56.73v
Versions Hardware Firmware Software SerialNo
5.3 5.9.47 2.17.9 308317320
OpStatus AuthMode CMU Mode
Idle Default Normal
SysFaults: Nil
Live status information
Min @ ID Max @ ID Avg Repeat
CellVolt 4.10v @ 1 4.10v @ 2 4.10v 6700
CellTemp 21ºC@ 1 23ºC@ 6 21ºC
BypassAmp 0.00A @ 0 0.00A @ 0
BypassTemp 25ºC@ 1 25ºC@ 1
BypSession 59.1mAh@ 3 199.8mAh@ 8
Total Overdue +Final +Initial InBypass
NumOfCells 14 0 0 0 0
SoC% Temp Volt Amp
Shunt 99.5% 42ºC 57.48v 0.007A
ToEmpty ToFull
Nom Capacity 799.757 0.243
Est Duration 40.9d 8.0d
Recent Consume 0.106 0.000
Expansion board
Input Run/Idle = off
Input Charge/Normal = off
Critical logic
control BattOK state
status LowAmbient,
Charging logic
control ON state
Idle Bypass: off
status BypassSessionLo, LowAmbient, PauseShuntSoC,
Discharging logic
control ON state
status LowAmbient,
Thermal Heating Logic
control OFF state
status LowAmbient,
Thermal Cooling Logic
control OFF state
status LowAmbient,
Remote Logic
ActV ActA TgtV TgtA state
Charge 0.0v 0.0A 57.5v 160.0A ON state
Dischg 0.0v 0.0A 47.6v 100.0A ON state
Daily Session information
Min Max
CellVolt 3.97 4.13
Thermal 20 23
ShuntSoc 70.0 100.5
ShuntVolt 51.69 57.60
SupplyVolt 46.96 57.37
Critical Events 3
Charge Dischg
ShuntPeak 124.58 66.79
Cumulative 227.756 91.476
Banding(hr) A B C D E F G H
SoC% 2.6 1.1 5.4 6.1 0.0 0.0 0.0 0.0
Thermal 0.0 0.0 0.0 0.0 15.1 0.0 0.0 0.1
Cell Node information
ID Bypass Initial Session Amp MinV MaxV MaxT BypT HiT HiBypT LoV HiV BypV BypA DatEr Reset CalV RepCV Serial HwVers
1 14/11/2021 1:38:38 PM 72.9 mAh 0.00A 4.10v 4.10v 21°C 25°C 55°C 75°C 2.90v 4.20v 4.10v 0.60A 0 0 0 250 308317320 HW5.3 FW5.9
2 14/11/2021 1:40:21 PM 74.9 mAh 0.00A 4.10v 4.10v 21°C 25°C 55°C 75°C 2.90v 4.20v 4.10v 0.60A 0 0 0 250 308317320 HW5.3 FW5.9
3 14/11/2021 1:40:20 PM 59.1 mAh 0.00A 4.10v 4.10v 21°C 25°C 55°C 75°C 2.90v 4.20v 4.10v 0.60A 0 0 0 250 308317320 HW5.3 FW5.9
4 14/11/2021 1:40:19 PM 66.8 mAh 0.00A 4.10v 4.10v 21°C 25°C 55°C 75°C 2.90v 4.20v 4.10v 0.60A 0 0 0 250 308317320 HW5.3 FW5.9
5 14/11/2021 1:40:21 PM 66.8 mAh 0.00A 4.10v 4.10v 21°C 25°C 55°C 75°C 2.90v 4.20v 4.10v 0.60A 0 0 0 250 308317320 HW5.3 FW5.9
6 14/11/2021 1:40:25 PM 61.4 mAh 0.00A 4.10v 4.10v 23°C 25°C 55°C 75°C 2.90v 4.20v 4.10v 0.60A 0 0 0 250 308317320 HW5.3 FW5.9
7 14/11/2021 1:38:36 PM 96.0 mAh 0.00A 4.10v 4.10v 23°C 25°C 55°C 75°C 2.90v 4.20v 4.10v 0.60A 0 0 0 250 308317320 HW5.3 FW5.9
8 14/11/2021 1:40:20 PM 199.8 mAh 0.00A 4.10v 4.10v 23°C 25°C 55°C 75°C 2.90v 4.20v 4.10v 0.60A 0 0 0 250 308317320 HW5.3 FW5.9
9 14/11/2021 1:40:03 PM 129.5 mAh 0.00A 4.10v 4.10v 23°C 25°C 55°C 75°C 2.90v 4.20v 4.10v 0.60A 0 0 0 250 308317320 HW5.3 FW5.9
10 14/11/2021 1:40:24 PM 70.6 mAh 0.00A 4.10v 4.10v 22°C 25°C 55°C 75°C 2.90v 4.20v 4.10v 0.60A 0 0 0 250 308317320 HW5.3 FW5.9
11 14/11/2021 1:40:21 PM 95.8 mAh 0.00A 4.10v 4.10v 22°C 25°C 55°C 75°C 2.90v 4.20v 4.10v 0.60A 0 0 0 250 308317320 HW5.3 FW5.9
12 14/11/2021 1:40:22 PM 134.4 mAh 0.00A 4.10v 4.10v 22°C 25°C 55°C 75°C 2.90v 4.20v 4.10v 0.60A 0 0 0 250 308317320 HW5.3 FW5.9
13 14/11/2021 1:40:19 PM 116.1 mAh 0.00A 4.10v 4.10v 22°C 25°C 55°C 75°C 2.90v 4.20v 4.10v 0.60A 0 0 0 250 308317320 HW5.3 FW5.9
14 14/11/2021 1:40:25 PM 87.9 mAh 0.00A 4.10v 4.10v 22°C 25°C 55°C 75°C 2.90v 4.20v 4.10v 0.60A 0 0 0 250 308317320 HW5.3 FW5.9
slimf
Here is the setup part of the log:
Setup configuration extract
???<?xml version="1.0" encoding="utf-8"?>
<WatchMonDeviceSettings xmlns:xsi="http://www.w3.org/2001/XMLSchema-instance" xmlns:xsd="http://www.w3.org/2001/XMLSchema">
<System>
<SetupVers>6</SetupVers>
<PresetID>9</PresetID>
<SystemID>4795</SystemID>
<SysCode>SYS4795</SysCode>
<SysName>Tower of Power</SysName>
<AssetCode>.</AssetCode>
<HubID>32354</HubID>
<HardwareVers>1283</HardwareVers>
<SerialNo>308317320</SerialNo>
<FirmwareVers>1289</FirmwareVers>
<BuildNo>47</BuildNo>
<AllowWebAuth>true</AllowWebAuth>
<AllowQuickSess>true</AllowQuickSess>
<QuickSessIntl>60000</QuickSessIntl>
</System>
<CellGroup>
<SetupVers>74</SetupVers>
<BattTypeID>LiIonLongLife</BattTypeID>
<FirstNodeID>1</FirstNodeID>
<LastNodeID>14</LastNodeID>
<NomCellVolt>3.7</NomCellVolt>
<LoCellVolt>2.9</LoCellVolt>
<HiCellVolt>4.2</HiCellVolt>
<BypassVoltLevel>4.1</BypassVoltLevel>
<BypassAmpLimit>0.6</BypassAmpLimit>
<BypassTempLimit>75</BypassTempLimit>
<LoCellTemp>-5</LoCellTemp>
<HiCellTemp>55</HiCellTemp>
<LoIgnoreTemp>-40</LoIgnoreTemp>
<EntireFirstNodeID>1</EntireFirstNodeID>
<EntireLastNodeID>14</EntireLastNodeID>
<NomCellsInSeries>14</NomCellsInSeries>
<CellMonTypeID>opt8</CellMonTypeID>
<BypassImpedance>4</BypassImpedance>
<BypassExtraInterval>25000</BypassExtraInterval>
<BypassLoVoltCutout>3.9</BypassLoVoltCutout>
<BypassShuntCharge>2.5</BypassShuntCharge>
<BypassShuntDischg>3.5</BypassShuntDischg>
<BypassShuntSocLo>85.0</BypassShuntSocLo>
<BypassCellVoltBand>0.05</BypassCellVoltBand>
<BypassCellVoltDiff>0.01</BypassCellVoltDiff>
<BypassStableInterval>6000</BypassStableInterval>
<BypassExtraAmp>0.5</BypassExtraAmp>
</CellGroup>
<Shunt>
<SetupVers>40</SetupVers>
<NomCapacity_mAh>800000</NomCapacity_mAh>
<DischgIdle>0.18</DischgIdle>
<ChargeIdle>0.15</ChargeIdle>
<SocCountLo>35.0</SocCountLo>
<SocCountHi>85.0</SocCountHi>
<SocLoRecal>-1.5</SocLoRecal>
<SocHiRecal>101.5</SocHiRecal>
<ReverseFlow>true</ReverseFlow>
<MonitorSocLoRecal>true</MonitorSocLoRecal>
<MonitorSocHiRecal>true</MonitorSocHiRecal>
<MonitorInBypassRecal>true</MonitorInBypassRecal>
<FilterVolt>none</FilterVolt>
<FilterAmp>none</FilterAmp>
<ShuntTypeID>ShuntMon2_A</ShuntTypeID>
<scale16_volt>100</scale16_volt>
<scale16_amp>100</scale16_amp>
<scale16_pw>1000</scale16_pw>
<Max16_Volt>65000</Max16_Volt>
<Max16_Charge>50000</Max16_Charge>
<Max16_Dischg>50000</Max16_Dischg>
<Max16Pw_Charge>30000</Max16Pw_Charge>
<Max16Pw_Dischg>30000</Max16Pw_Dischg>
<granularity_volt>0.00223769</granularity_volt>
<granularity_amp>0.00186163</granularity_amp>
<granularity_mAh>5.17119E-10</granularity_mAh>
<granularity_celcius>1</granularity_celcius>
<granularity_va>4.1658E-11</granularity_va>
<granularity_vah>1.1572E-17</granularity_vah>
</Shunt>
<ShuntDevice>
<SerialNo>268228545</SerialNo>
<ManuCode>1414807874</ManuCode>
<PartNum>513</PartNum>
<VersCode>1</VersCode>
<Pns1>500A</Pns1>
<Pns2>50mR</Pns2>
</ShuntDevice>
<ShuntMetrics>
<SetupVers>14</SetupVers>
<ShuntSocCycles>18</ShuntSocCycles>
<hasShuntSocCountHi>true</hasShuntSocCountHi>
<lastTimeSocCountLo>2021-11-10T19:46:17Z</lastTimeSocCountLo>
<lastTimeSocCountHi>2021-11-12T14:28:29Z</lastTimeSocCountHi>
<lastTimeSocLoRecal>2021-01-03T21:57:41Z</lastTimeSocLoRecal>
<lastTimeSocHiRecal>2021-11-14T14:03:28Z</lastTimeSocHiRecal>
<lastTimeAcculmSave>2021-11-14T15:05:55Z</lastTimeAcculmSave>
</ShuntMetrics>
<Expansion>
<SetupVers>10</SetupVers>
<Out09>CriticalFault</Out09>
<ExtensionTemplate>WatchMon5expR1</ExtensionTemplate>
</Expansion>
<CommsCh>
<SetupVers>7</SetupVers>
<CanbusMode>VictronCC</CanbusMode>
<CanbusTxBroadcast>true</CanbusTxBroadcast>
<WifiUdpTxBroadcast>true</WifiUdpTxBroadcast>
<WifiBroadcastMode>Verbose</WifiBroadcastMode>
<MqttBroadcastMode>mode0</MqttBroadcastMode>
</CommsCh>
<MqttProp>
<MqttProfile>profile0</MqttProfile>
<SecureMethod>mode0</SecureMethod>
</MqttProp>
<Critical>
<SetupVers>20</SetupVers>
<ControlMode>Auto</ControlMode>
<StopTimerInterval>45000</StopTimerInterval>
<StartTimerInterval>120000</StartTimerInterval>
<TimeoutManualOverride>300000</TimeoutManualOverride>
<PrechargeTimeInterval>2000</PrechargeTimeInterval>
<AutoRecovery>true</AutoRecovery>
<CellVoltLo>2.7</CellVoltLo>
<CellVoltHi>4.2</CellVoltHi>
<CellTempLo>-10</CellTempLo>
<CellTempHi>55</CellTempHi>
<SupplyVoltLo>37.8</SupplyVoltLo>
<SupplyVoltHi>58.8</SupplyVoltHi>
<AmbientTempLo>-15</AmbientTempLo>
<AmbientTempHi>65</AmbientTempHi>
<ShuntVoltLo>37.8</ShuntVoltLo>
<ShuntVoltHi>58.8</ShuntVoltHi>
<ShuntVoltLoIdle>51.8</ShuntVoltLoIdle>
<ShuntCrateCharge>0.8</ShuntCrateCharge>
<ShuntCrateDischg>0.8</ShuntCrateDischg>
<ShuntPeakCharge>500</ShuntPeakCharge>
<ShuntPeakDischg>500</ShuntPeakDischg>
<RecoverShuntChargeLimit>2</RecoverShuntChargeLimit>
<RecoverShuntDischgLimit>15</RecoverShuntDischgLimit>
<MonitorCellVoltHi>true</MonitorCellVoltHi>
<MonitorCellVoltLo>true</MonitorCellVoltLo>
<MonitorCellTempHi>true</MonitorCellTempHi>
<MonitorCellTempLo>true</MonitorCellTempLo>
<MonitorShuntVoltLo>true</MonitorShuntVoltLo>
<MonitorShuntVoltHi>true</MonitorShuntVoltHi>
</Critical>
<Charge>
<SetupVers>119</SetupVers>
<StopTimerInterval>5000</StopTimerInterval>
<StartTimerInterval>60000</StartTimerInterval>
<AllowLimPowerStage>true</AllowLimPowerStage>
<AllowBypassLimPower>true</AllowBypassLimPower>
<AllowBypassComplete>true</AllowBypassComplete>
<AllowBypassSession>true</AllowBypassSession>
<InitalBypassAmp>0.3</InitalBypassAmp>
<FinalBypassAmp>0.1</FinalBypassAmp>
<BypassSessionLo>50</BypassSessionLo>
<CellVoltHi>4.15</CellVoltHi>
<CellVoltResume>4.15</CellVoltResume>
<CellVoltLimPower>3.4</CellVoltLimPower>
<CellTempHi>45</CellTempHi>
<AmbientTempLo>-5</AmbientTempLo>
<AmbientTempHi>55</AmbientTempHi>
<SupplyVoltHi>58.1</SupplyVoltHi>
<SupplyVoltResume>57</SupplyVoltResume>
<ShuntVoltHi>58.1</ShuntVoltHi>
<ShuntVoltResume>57</ShuntVoltResume>
<ShuntVoltLimPower>47.6</ShuntVoltLimPower>
<ShuntSocHi>100.0</ShuntSocHi>
<ShuntSocResume>95.0</ShuntSocResume>
</Charge>
<Discharge>
<SetupVers>3</SetupVers>
<StartTimerInterval>20000</StartTimerInterval>
<CellVoltLo>3.4</CellVoltLo>
<CellVoltResume>3.7</CellVoltResume>
<CellTempLo>-5</CellTempLo>
<CellTempHi>50</CellTempHi>
<AmbientTempLo>-10</AmbientTempLo>
<AmbientTempHi>60</AmbientTempHi>
<SupplyVoltLo>9</SupplyVoltLo>
<SupplyVoltResume>9</SupplyVoltResume>
<ShuntVoltLo>47.6</ShuntVoltLo>
<ShuntVoltResume>49.7</ShuntVoltResume>
<ShuntSocLo>20.0</ShuntSocLo>
<ShuntSocResume>25.0</ShuntSocResume>
</Discharge>
<Thermal>
<SetupVers>8</SetupVers>
<ControlModeCool>Auto</ControlModeCool>
<StopTimerIntervalCool>60000</StopTimerIntervalCool>
<StartTimerIntervalCool>30000</StartTimerIntervalCool>
<HiCellTemp>35</HiCellTemp>
<HiAmbientTemp>40</HiAmbientTemp>
<HiCellTempCutout>10</HiCellTempCutout>
<HiAmbientCutout>5</HiAmbientCutout>
<MonitorHiCellTemp>true</MonitorHiCellTemp>
<MonitorInBypass>true</MonitorInBypass>
<ControlModeHeat>Auto</ControlModeHeat>
<StopTimerIntervalHeat>60000</StopTimerIntervalHeat>
<StartTimerIntervalHeat>45000</StartTimerIntervalHeat>
<LoCellTemp>5</LoCellTemp>
<LoCellTempCutout>30</LoCellTempCutout>
<LoAmbientCutout>35</LoAmbientCutout>
<MonitorLoCellTemp>true</MonitorLoCellTemp>
</Thermal>
<Remote>
<RemoteTemplate>opt1</RemoteTemplate>
<Charge>
<NormVolt>575</NormVolt>
<NormAmp>1600</NormAmp>
<LimpVolt>574</LimpVolt>
<LimpAmp>5</LimpAmp>
<scale16_volt>10</scale16_volt>
<scale16_amp>10</scale16_amp>
<scale16_va>1</scale16_va>
</Charge>
<Discharge>
<NormVolt>476</NormVolt>
<NormAmp>1000</NormAmp>
</Discharge>
</Remote>
<Scheduler>
<SetupVers>1</SetupVers>
<Sun>VVVVVVVVVVVVVVVVVVVVVVVVVVVVVVVV</Sun>
<Mon>VVVVVVVVVVVVVVVVVVVVVVVVVVVVVVVV</Mon>
<Tues>VVVVVVVVVVVVVVVVVVVVVVVVVVVVVVVV</Tues>
<Wed>VVVVVVVVVVVVVVVVVVVVVVVVVVVVVVVV</Wed>
<Thurs>VVVVVVVVVVVVVVVVVVVVVVVVVVVVVVVV</Thurs>
<Fri>VVVVVVVVVVVVVVVVVVVVVVVVVVVVVVVV</Fri>
<Sat>VVVVVVVVVVVVVVVVVVVVVVVVVVVVVVVV</Sat>
</Scheduler>
<SocLimit>
<SetupVers>4</SetupVers>
<BasedOn1>mode1</BasedOn1>
<SocLo1>80.0</SocLo1>
<SocHi1>102.0</SocHi1>
<SocLoCut1>79.5</SocLoCut1>
<SocHiCut1>102.5</SocHiCut1>
<BasedOn2>mode1</BasedOn2>
<SocLo2>30.0</SocLo2>
<SocHi2>80.0</SocHi2>
<SocLoCut2>29.5</SocLoCut2>
<SocHiCut2>80.5</SocHiCut2>
<BasedOn3>mode1</BasedOn3>
<SocLo3>-2.0</SocLo3>
<SocHi3>30.0</SocHi3>
<SocLoCut3>-2.5</SocLoCut3>
<SocHiCut3>30.5</SocHiCut3>
<BasedOn4>none</BasedOn4>
</SocLimit>
<Lifetime>
<FirstSyncTime>1970-01-01T00:00:00Z</FirstSyncTime>
<StartupTime>0001-01-01T00:00:00</StartupTime>
<Count_Startup>26</Count_Startup>
<Count_CriticalBattOk>24</Count_CriticalBattOk>
<Count_ChargeOn>3245</Count_ChargeOn>
<Count_ChargeLimp>2934</Count_ChargeLimp>
<Count_DischgOn>68</Count_DischgOn>
<Count_HeatOn>3</Count_HeatOn>
<Count_CoolOn>46</Count_CoolOn>
<Count_DailySession>362</Count_DailySession>
<RecentTime_CriticalOn>2021-11-14T14:05:29Z</RecentTime_CriticalOn>
<RecentTime_CriticalOff>2021-11-14T13:55:57Z</RecentTime_CriticalOff>
<RecentTime_ChargeOn>2021-11-14T14:04:29Z</RecentTime_ChargeOn>
<RecentTime_ChargeOff>2021-11-03T22:33:55Z</RecentTime_ChargeOff>
<RecentTime_ChargeLimp>2021-11-14T13:54:28Z</RecentTime_ChargeLimp>
<RecentTime_DischgOn>2021-11-14T13:36:07Z</RecentTime_DischgOn>
<RecentTime_DischgOff>2021-04-09T08:24:20Z</RecentTime_DischgOff>
<RecentTime_DischgLimp>1970-01-01T00:00:00Z</RecentTime_DischgLimp>
<RecentTime_AltChargeOn>1970-01-01T00:00:00Z</RecentTime_AltChargeOn>
<RecentTime_AltChargeOff>1970-01-01T00:00:00Z</RecentTime_AltChargeOff>
<RecentTime_AltDischgOn>1970-01-01T00:00:00Z</RecentTime_AltDischgOn>
<RecentTime_AltDischgOff>1970-01-01T00:00:00Z</RecentTime_AltDischgOff>
<RecentTime_HeatOn>2020-11-08T13:01:44Z</RecentTime_HeatOn>
<RecentTime_HeatOff>1970-01-01T00:00:00Z</RecentTime_HeatOff>
<RecentTime_CoolOn>2020-12-31T17:19:47Z</RecentTime_CoolOn>
<RecentTime_CoolOff>2020-12-31T20:15:26Z</RecentTime_CoolOff>
<RecentTime_BypassInitial>2021-11-14T11:46:47Z</RecentTime_BypassInitial>
<RecentTime_BypassComplete>2021-11-14T13:15:05Z</RecentTime_BypassComplete>
<RecentTime_BypassTest>1970-01-01T00:00:00Z</RecentTime_BypassTest>
<BypassOutcome>NotTested</BypassOutcome>
<RecentTime_WizardSetup>2021-03-20T17:13:57Z</RecentTime_WizardSetup>
<RecentTime_BypassExtra>1970-01-01T00:00:00Z</RecentTime_BypassExtra>
<RecentTime_SocLimit1On>1970-01-01T00:00:00Z</RecentTime_SocLimit1On>
<RecentTime_SocLimit1Off>1970-01-01T00:00:00Z</RecentTime_SocLimit1Off>
<RecentTime_SocLimit2On>1970-01-01T00:00:00Z</RecentTime_SocLimit2On>
<RecentTime_SocLimit2Off>1970-01-01T00:00:00Z</RecentTime_SocLimit2Off>
<RecentTime_SocLimit3On>1970-01-01T00:00:00Z</RecentTime_SocLimit3On>
<RecentTime_SocLimit3Off>1970-01-01T00:00:00Z</RecentTime_SocLimit3Off>
<RecentTime_SocLimit4On>1970-01-01T00:00:00Z</RecentTime_SocLimit4On>
<RecentTime_SocLimit4Off>1970-01-01T00:00:00Z</RecentTime_SocLimit4Off>
</Lifetime>
<CellNodes>
<Item>
<ID>1</ID>
<BypV>4.1</BypV>
<Vers>HW5.3 FW5.9</Vers>
</Item>
<Item>
<ID>2</ID>
<BypV>4.1</BypV>
</Item>
<Item>
<ID>3</ID>
<BypV>4.1</BypV>
</Item>
<Item>
<ID>4</ID>
<BypV>4.1</BypV>
</Item>
<Item>
<ID>5</ID>
<BypV>4.1</BypV>
</Item>
<Item>
<ID>6</ID>
<BypV>4.1</BypV>
</Item>
<Item>
<ID>7</ID>
<BypV>4.1</BypV>
</Item>
<Item>
<ID>8</ID>
<BypV>4.1</BypV>
</Item>
<Item>
<ID>9</ID>
<BypV>4.1</BypV>
</Item>
<Item>
<ID>10</ID>
<BypV>4.1</BypV>
</Item>
<Item>
<ID>11</ID>
<BypV>4.1</BypV>
</Item>
<Item>
<ID>12</ID>
<BypV>4.1</BypV>
</Item>
<Item>
<ID>13</ID>
<BypV>4.1</BypV>
</Item>
<Item>
<ID>14</ID>
<BypV>4.1</BypV>
</Item>
</CellNodes>
</WatchMonDeviceSettings>
Test without charge logic - also you could try removing mons and see if it still trips, i had one with a bad cable to my long mons (gecho shit + damage)
slimf
Hi Peter
I have WM5 - So I cant test without Longmons :)
When you say test without charge logic - Do you mean just disable everything in the screenshot?
slimf
The mystry deepens - I did a log extract, and it appears that the shunt times out before throwing a critical fault..
LogID LogDate LogTime MinCellVolt MaxCellVolt AvgCellVolt AvgCellTemp SocHiRes ShuntVolt ShuntAmp NumInBypass OpState ControlLogic
# yyyy-MM-dd HH:mm:ss Volt Volt Volt ºC %Perc Volt Amp # # #
10000 2021-11-14 12:15:47 4.08 4.10 4.09 20 93.22 57.40 83.92 0 Charging 11010000
10001 2021-11-14 12:16:47 4.09 4.10 4.09 20 93.36 57.36 60.39 0 Charging 10110000
10002 2021-11-14 12:17:47 4.09 4.11 4.09 20 93.50 57.39 66.77 2 Charging 10110000
10003 2021-11-14 12:18:47 4.09 4.10 4.09 20 93.64 57.39 63.59 0 Charging 10110000
10004 2021-11-14 12:19:47 4.09 4.10 4.09 20 93.77 57.39 65.45 0 Charging 11010000
10005 2021-11-14 12:20:47 4.09 4.11 4.09 20 93.91 57.41 62.42 2 Charging 10110000
10006 2021-11-14 12:21:47 4.09 4.11 4.09 20 94.03 57.41 62.19 2 Charging 10110000
10007 2021-11-14 12:22:47 4.09 4.11 4.09 20 94.16 57.43 62.73 2 Charging 10110000
10008 2021-11-14 12:23:47 4.09 4.11 4.09 20 94.29 57.44 62.86 2 Charging 10110000
10009 2021-11-14 12:24:47 4.09 4.11 4.09 20 94.43 57.45 63.02 2 Charging 10110000
10010 2021-11-14 12:25:47 4.09 4.11 4.10 20 94.56 57.46 62.61 2 Charging 10110000
10011 2021-11-14 12:26:47 4.09 4.11 4.10 20 94.69 57.46 63.34 2 Charging 10110000
10012 2021-11-14 12:27:47 4.09 4.11 4.10 20 94.82 57.48 63.43 2 Charging 10110000
10013 2021-11-14 12:28:47 4.10 4.11 4.10 20 94.95 57.49 63.24 2 Charging 10110000
10014 2021-11-14 12:29:47 4.09 4.11 4.10 20 95.05 57.49 66.33 2 Charging 10110000
10015 2021-11-14 12:30:47 4.10 4.11 4.10 21 95.19 57.51 65.08 2 Charging 10110000
10016 2021-11-14 12:31:47 4.10 4.11 4.10 21 95.32 57.53 64.12 2 Charging 10110000
10017 2021-11-14 12:32:48 4.10 4.12 4.10 21 95.46 57.54 64.67 2 Charging 10110000
10018 2021-11-14 12:33:48 4.10 4.12 4.10 21 95.59 57.55 64.08 2 Charging 10110000
10019 2021-11-14 12:34:48 4.10 4.12 4.10 21 95.72 57.44 5.41 3 Charging 10110000
10020 2021-11-14 12:35:48 4.10 4.10 4.10 21 95.76 57.45 25.46 0 Charging 10110000
10021 2021-11-14 12:36:48 4.10 4.11 4.10 21 95.85 57.52 50.95 2 Charging 10110000
10022 2021-11-14 12:37:48 4.10 4.11 4.10 21 95.94 57.52 51.74 1 Charging 10110000
10023 2021-11-14 12:38:48 4.10 4.12 4.10 21 96.00 57.55 63.71 2 Charging 10110000
10024 2021-11-14 12:39:48 4.10 4.11 4.10 21 96.12 57.56 61.42 2 Charging 10110000
10025 2021-11-14 12:40:48 4.09 4.10 4.09 21 96.15 57.44 11.50 0 Charging 10110000
10026 2021-11-14 12:41:48 4.10 4.11 4.10 21 96.21 57.53 52.35 2 Charging 10110000
10027 2021-11-14 12:42:48 4.10 4.10 4.10 21 96.32 57.48 19.21 0 Charging 10110000
10028 2021-11-14 12:43:48 4.10 4.10 4.10 21 96.38 57.48 17.20 0 Charging 10110000
10029 2021-11-14 12:44:48 4.10 4.10 4.10 21 96.41 57.45 10.77 0 Charging 11010000
10030 2021-11-14 12:45:48 4.10 4.11 4.10 21 96.45 57.55 68.73 2 Charging 11010000
10031 2021-11-14 12:46:48 4.10 4.12 4.10 21 96.53 57.57 71.09 3 Charging 10110000
10032 2021-11-14 12:47:48 4.10 4.10 4.10 21 96.64 57.48 12.06 0 Charging 10110000
10033 2021-11-14 12:48:48 4.10 4.10 4.10 21 96.67 57.48 18.72 0 Charging 11010000
10034 2021-11-14 12:49:48 4.10 4.11 4.10 21 96.73 57.52 33.04 2 Charging 10110000
10035 2021-11-14 12:50:48 4.10 4.11 4.10 21 96.80 57.52 29.78 2 Charging 10110000
10036 2021-11-14 12:51:48 4.10 4.11 4.10 21 96.86 57.52 28.07 2 Charging 10110000
10037 2021-11-14 12:52:48 4.10 4.11 4.10 21 96.92 57.53 28.24 2 Charging 10110000
10038 2021-11-14 12:53:48 4.10 4.11 4.10 21 96.97 57.53 26.43 2 Charging 10110000
10039 2021-11-14 12:54:48 4.10 4.10 4.10 21 97.02 57.46 -8.28 0 Discharging 10110000
10040 2021-11-14 12:55:48 4.10 4.11 4.10 21 97.05 57.54 34.82 2 Charging 10110000
10041 2021-11-14 12:56:48 4.10 4.11 4.10 21 97.12 57.54 26.70 2 Charging 10110000
10042 2021-11-14 12:57:48 4.09 4.10 4.09 21 97.10 57.43 -12.03 0 Discharging 10110000
10043 2021-11-14 12:58:48 4.10 4.10 4.10 21 97.10 57.46 8.96 0 Charging 11010000
10044 2021-11-14 12:59:48 4.10 4.11 4.10 21 97.14 57.52 29.83 2 Charging 10110000
10045 2021-11-14 13:00:48 4.10 4.11 4.10 21 97.21 57.54 25.15 2 Charging 10110000
10046 2021-11-14 13:01:48 4.10 4.11 4.10 21 97.28 57.57 36.12 2 Charging 10110000
10047 2021-11-14 13:02:48 4.10 4.11 4.11 21 97.36 57.61 43.75 6 Charging 10110000
10048 2021-11-14 13:03:48 4.11 4.11 4.11 21 97.44 57.56 18.75 7 Charging 10110000
10049 2021-11-14 13:04:48 4.10 4.11 4.10 21 97.46 57.54 18.80 3 Charging 10110000
10050 2021-11-14 13:05:48 4.09 4.10 4.09 21 97.43 57.44 -13.57 0 Discharging 10110000
10051 2021-11-14 13:06:48 4.10 4.11 4.10 21 97.48 57.57 40.83 6 Charging 10110000
10052 2021-11-14 13:07:48 4.10 4.11 4.11 21 97.54 57.56 22.12 7 Charging 10110000
10053 2021-11-14 13:08:48 4.10 4.11 4.10 21 97.58 57.54 17.48 7 Charging 10110000
10054 2021-11-14 13:09:48 4.10 4.11 4.10 21 97.62 57.55 22.07 7 Charging 10110000
10055 2021-11-14 13:10:49 4.09 4.10 4.10 21 97.62 57.44 -28.46 0 Discharging 10110000
10056 2021-11-14 13:11:49 4.09 4.10 4.09 21 97.60 57.44 -17.83 0 Discharging 10110000
10057 2021-11-14 13:12:49 4.10 4.12 4.11 21 97.64 57.58 37.80 7 Charging 10110000
10058 2021-11-14 13:13:49 4.11 4.11 4.11 21 97.70 57.55 20.32 7 Charging 10110000
10059 2021-11-14 13:14:49 4.10 4.11 4.10 21 97.73 57.54 12.72 7 Charging 10110000
10060 2021-11-14 13:15:49 4.10 4.11 4.10 21 99.99 0.00 0.00 6 ShuntTimeout 10110000
10061 2021-11-14 13:16:49 4.10 4.11 4.10 21 99.99 0.00 0.00 2 ShuntTimeout 00110000
10062 2021-11-14 13:17:49 4.10 4.11 4.10 21 99.99 0.00 0.00 1 ShuntTimeout 00110000
10063 2021-11-14 13:18:49 4.10 4.10 4.10 21 99.99 57.48 -0.09 0 CriticalOffline 00110000
10064 2021-11-14 13:19:49 4.10 4.10 4.10 21 99.99 57.48 -0.04 0 CriticalOffline 01010000
10065 2021-11-14 13:20:49 4.10 4.10 4.10 21 99.99 57.48 0.02 0 Idle 11010000
10066 2021-11-14 13:21:49 4.10 4.10 4.10 21 99.99 57.49 0.01 0 Idle 11010000
10067 2021-11-14 13:22:49 4.10 4.10 4.10 21 99.99 57.47 0.01 0 Idle 11010000
10068 2021-11-14 13:23:49 4.10 4.10 4.10 21 99.99 57.47 0.01 0 Idle 11010000
10069 2021-11-14 13:24:49 4.10 4.10 4.10 21 99.99 57.49 0.01 0 Idle 11010000
10070 2021-11-14 13:25:49 4.10 4.10 4.10 21 99.99 57.49 0.02 0 Idle 11010000
10071 2021-11-14 13:26:49 4.10 4.10 4.10 21 99.99 57.48 0.01 0 Idle 11010000
10072 2021-11-14 13:27:49 4.10 4.10 4.10 21 99.99 57.48 0.01 0 Idle 11010000
10073 2021-11-14 13:28:49 4.10 4.10 4.10 21 99.99 57.46 -0.01 0 Idle 11010000
10074 2021-11-14 13:29:49 4.10 4.10 4.10 21 99.99 57.46 0.01 0 Idle 11010000
10075 2021-11-14 13:30:49 4.10 4.10 4.10 21 99.99 57.48 -0.01 0 Idle 11010000
10076 2021-11-14 13:31:49 4.10 4.10 4.10 21 99.99 57.47 0.00 0 Idle 11010000
10077 2021-11-14 13:32:49 4.10 4.10 4.10 21 99.99 57.48 0.03 0 Idle 11010000
10078 2021-11-14 13:33:49 4.10 4.10 4.10 21 99.99 57.47 0.03 0 Idle 11010000
10079 2021-11-14 13:34:49 4.10 4.10 4.10 21 99.99 57.45 -0.01 0 Idle 11010000
10080 2021-11-14 13:36:37 4.09 4.10 4.09 21 99.99 57.45 -0.14 0 Idle 10010000
10081 2021-11-14 13:37:52 4.09 4.10 4.09 21 99.99 57.45 -0.09 0 Idle 11010000
10082 2021-11-14 13:38:52 4.10 4.10 4.10 21 100.02 57.47 -0.39 0 Discharging 10110000
10083 2021-11-14 13:39:52 4.10 4.10 4.10 21 100.02 57.49 19.26 0 Charging 11010000
10084 2021-11-14 13:40:52 4.11 4.13 4.11 21 100.15 57.67 67.04 7 Charging 10110000
10085 2021-11-14 13:41:52 4.11 4.11 4.11 21 100.22 57.57 16.93 7 Charging 10110000
10086 2021-11-14 13:42:52 4.10 4.11 4.10 21 100.23 57.52 4.21 1 Charging 10110000
10087 2021-11-14 13:43:52 4.11 4.12 4.11 21 100.29 57.65 57.74 7 Charging 10110000
10088 2021-11-14 13:44:52 4.10 4.11 4.10 21 100.32 57.50 -15.55 5 Discharging 10110000
10089 2021-11-14 13:45:52 4.09 4.10 4.10 21 100.29 57.48 -6.98 0 Discharging 10110000
10090 2021-11-14 13:46:52 4.10 4.10 4.10 21 100.30 57.52 11.52 0 Charging 11010000
10091 2021-11-14 13:47:52 4.10 4.11 4.10 21 100.33 57.55 15.00 1 Charging 10110000
10092 2021-11-14 13:48:52 4.10 4.11 4.10 21 100.36 57.55 15.00 1 Charging 10110000
10093 2021-11-14 13:49:52 4.10 4.11 4.10 21 100.39 57.56 14.24 4 Charging 10110000
10094 2021-11-14 13:50:52 4.11 4.12 4.11 21 100.47 57.64 41.76 7 Charging 10110000
10095 2021-11-14 13:51:53 4.11 4.12 4.11 21 100.52 57.62 29.30 7 Full 10110000
10096 2021-11-14 13:52:53 4.10 4.11 4.10 21 100.55 57.52 -18.72 7 Full 10110000
10097 2021-11-14 13:53:53 4.08 4.10 4.10 21 100.49 57.44 -33.41 0 Discharging 10110000
10098 2021-11-14 13:54:53 4.10 4.11 4.10 21 100.48 57.52 5.30 1 Charging 10110000
10099 2021-11-14 13:55:53 4.11 4.11 4.11 21 99.99 0.00 0.00 7 ShuntTimeout 10110000
10100 2021-11-14 13:56:53 4.10 4.11 4.10 21 99.99 0.00 0.00 3 ShuntTimeout 00110000
10101 2021-11-14 13:57:53 4.10 4.11 4.10 21 99.99 0.00 0.00 3 ShuntTimeout 00110000
10102 2021-11-14 13:58:53 4.10 4.11 4.10 21 99.99 0.00 0.00 3 ShuntTimeout 00110000
10103 2021-11-14 13:59:53 4.10 4.11 4.10 21 99.99 0.00 0.00 2 ShuntTimeout 00110000
10104 2021-11-14 14:00:53 4.10 4.11 4.10 21 99.99 0.00 0.00 2 ShuntTimeout 00110000
10105 2021-11-14 14:01:53 4.10 4.11 4.10 21 99.99 0.00 0.00 1 ShuntTimeout 00110000
10106 2021-11-14 14:02:53 4.10 4.11 4.10 21 99.99 0.00 0.00 1 ShuntTimeout 00110000
10107 2021-11-14 14:03:53 4.10 4.10 4.10 21 99.99 57.50 -0.31 0 CriticalOffline 00110000
10108 2021-11-14 14:04:53 4.10 4.10 4.10 21 99.99 57.50 -0.27 0 CriticalOffline 01010000
10109 2021-11-14 14:05:53 4.10 4.10 4.10 21 99.99 57.50 -0.22 0 Discharging 11010000
10110 2021-11-14 14:06:53 4.10 4.10 4.10 21 99.99 57.50 -0.22 0 Discharging 11010000
10111 2021-11-14 14:07:53 4.10 4.10 4.10 21 99.99 57.50 -0.22 0 Discharging 11010000
10112 2021-11-14 14:08:53 4.10 4.10 4.10 21 99.99 57.50 -0.23 0 Discharging 11010000
10113 2021-11-14 14:09:53 4.10 4.10 4.10 21 99.99 57.50 -0.23 0 Discharging 11010000
10114 2021-11-14 14:10:53 4.10 4.10 4.10 21 99.99 57.50 -0.25 0 Discharging 11010000
10115 2021-11-14 14:11:53 4.10 4.10 4.10 21 99.99 57.50 -0.28 0 Discharging 11010000
10116 2021-11-14 14:12:53 4.10 4.10 4.10 21 99.99 57.49 -0.26 0 Discharging 11010000
10117 2021-11-14 14:13:53 4.10 4.10 4.10 21 99.99 57.49 -0.28 0 Discharging 11010000
10118 2021-11-14 14:14:53 4.10 4.10 4.10 21 99.99 57.49 -0.26 0 Discharging 11010000
10119 2021-11-14 14:15:53 4.10 4.10 4.10 21 99.99 57.49 -0.26 0 Discharging 11010000
10120 2021-11-14 14:16:53 4.10 4.10 4.10 21 99.99 57.49 -0.27 0 Discharging 11010000
10121 2021-11-14 14:17:53 4.10 4.10 4.10 21 99.99 57.49 -0.27 0 Discharging 11010000
10122 2021-11-14 14:18:53 4.10 4.10 4.10 21 99.99 57.49 -0.27 0 Discharging 11010000
10123 2021-11-14 14:19:53 4.10 4.10 4.10 21 99.99 57.49 -0.28 0 Discharging 11010000
10124 2021-11-14 14:20:53 4.10 4.10 4.10 21 99.99 57.49 -0.26 0 Discharging 11010000
10125 2021-11-14 14:21:53 4.10 4.10 4.10 21 99.99 57.49 -0.25 0 Discharging 11010000
10126 2021-11-14 14:22:53 4.10 4.10 4.10 21 99.98 57.49 -0.25 0 Discharging 11010000
10127 2021-11-14 14:23:53 4.10 4.10 4.10 21 99.98 57.49 -0.25 0 Discharging 11010000
10128 2021-11-14 14:24:53 4.10 4.10 4.10 21 99.98 57.49 -0.25 0 Discharging 11010000
10129 2021-11-14 14:25:53 4.10 4.10 4.10 21 99.98 57.49 -0.24 0 Discharging 11010000
10130 2021-11-14 14:26:53 4.10 4.10 4.10 21 99.98 57.49 -0.25 0 Discharging 11010000
10131 2021-11-14 14:27:53 4.10 4.10 4.10 21 99.98 57.49 -0.25 0 Discharging 11010000
10132 2021-11-14 14:28:53 4.10 4.10 4.10 21 99.98 57.48 -0.25 0 Discharging 11010000
10133 2021-11-14 14:29:54 4.10 4.10 4.10 21 99.98 57.48 -0.25 0 Discharging 11010000
10134 2021-11-14 14:30:54 4.10 4.10 4.10 21 99.98 57.48 -0.26 0 Discharging 11010000
10135 2021-11-14 14:31:54 4.10 4.10 4.10 21 99.98 57.48 -0.25 0 Discharging 11010000
10136 2021-11-14 14:32:54 4.10 4.10 4.10 21 99.98 57.48 -0.26 0 Discharging 11010000
10137 2021-11-14 14:33:54 4.10 4.10 4.10 21 99.98 57.48 -0.26 0 Discharging 11010000
10138 2021-11-14 14:34:54 4.10 4.10 4.10 21 99.98 57.48 -0.25 0 Discharging 11010000
10139 2021-11-14 14:35:54 4.10 4.10 4.10 21 99.98 57.48 -0.25 0 Discharging 11010000
10140 2021-11-14 14:36:54 4.10 4.10 4.10 21 99.98 57.48 -0.26 0 Discharging 11010000
10141 2021-11-14 14:37:54 4.10 4.10 4.10 21 99.98 57.48 -0.25 0 Discharging 11010000
10142 2021-11-14 14:38:54 4.10 4.10 4.10 21 99.98 57.48 -0.24 0 Discharging 11010000
10143 2021-11-14 14:39:54 4.10 4.10 4.10 21 99.98 57.48 -0.23 0 Discharging 11010000
10144 2021-11-14 14:40:54 4.10 4.10 4.10 21 99.97 57.48 -0.23 0 Discharging 11010000
10145 2021-11-14 14:41:54 4.10 4.10 4.10 21 99.97 57.48 -0.18 0 Idle 11010000
10146 2021-11-14 14:42:54 4.10 4.10 4.10 21 99.97 57.48 -0.18 0 Discharging 11010000
10147 2021-11-14 14:43:54 4.10 4.10 4.10 21 99.97 57.48 -0.21 0 Discharging 11010000
10148 2021-11-14 14:44:54 4.10 4.10 4.10 21 99.97 57.48 -0.20 0 Discharging 11010000
10149 2021-11-14 14:45:54 4.10 4.10 4.10 21 99.97 57.48 -0.23 0 Discharging 11010000
10150 2021-11-14 14:46:54 4.10 4.10 4.10 21 99.97 57.48 -0.23 0 Discharging 11010000
10151 2021-11-14 14:47:54 4.10 4.10 4.10 21 99.97 57.47 -0.24 0 Discharging 11010000
10152 2021-11-14 14:48:54 4.10 4.10 4.10 21 99.97 57.47 -0.24 0 Discharging 11010000
10240 2021-11-07 15:39:07 4.03 4.03 4.03 24 85.88 56.55 -0.23 0 Discharging 11010000
so shunt losing signal?
slimf
Dunno - seems to be the case from the log - but there is no mention of this in their documentation - so not sure.
it’s been in service since Jan 26 2020 and is in a locked cupboard. Very short shunt cable (40cm maybe) - never seemed to be an issue before today. Weird.
First - when I've had trouble, Batrium support simply said... dump the log and look for the issue. Hmmmm... this never worked for me very well but it's their first advice - so..... :)
Looking thru your log (1st post) I see these 3 lines....
ShuntSoc 70.0 100.5
Critical Events 3
What's catching my eye is 'apparently' the shunt SoC is 100.5% in the 1st line, and SoC% of 0.0? in the 3rd line. I notice this because my own shunt does weird things about twice a year and when it goes to 0.0% the Batrium WM4 *does not like it* and the Shunt values stop reporting... and I have to manually reset the SoC% to get things working. Maybe this could be the issue for you as well? and the cause of Critical Events?
Bottom line, just a guess.... - monitor your shunt SoC for 100%+ and/or 0% occurrences and/or reset it manually to a reasonable value and see if the critical condition clears.
On the shunt misbehaving - there has been discussion threads on this suggesting interference as a source issue but I've not had a resolution for my own case. To give you an idea - here's a listing for the last 15 days or so of 6am voltage / SoC% from Batrium Shunt at that time/voltage. You would think 49.8v would have the same SoC % each time but it varies quite (14.6% to 21.3%) a bit for no reason I can determine BUT sometimes (twice a year) it just goes to 0.0% with no reason which causes problems.
slimf
Hi
Thanks - it is very weird. Since yesterday, it's been working fine again. Fingers crossed it's not something that keeps happening - As I really don't want my breaker breaking up to 160amps over and over.
One thing that was happening yesterday that may have caused 'noise' was a sunny day with clouds blowing over quite quickly (windy).. The system would go from say 100amps -> almost nothing and back up again quite quickly. Not sure if that had anything to do with it but thought I would mention it.
Hi
I agree about some weird things with Batrium. For me, Batrium will go weird / throw a fault *sometimes* if there's a heavy rain storm / humidity goes up rapidly. The unit is under the house with vents to the outside - so the humidity 'could'? be getting to it but its 8 ft from nearest vent.
BUT - maybe its actually clouds / major swings in amps as you suggest as this would occur along with a rain storm blowing in rapidly and make more sense that humidity.
slimf
Further to the problem on the 14th, I had had another critical event.. Here is the log
9129 2021-11-15 16:26:36 4.10 4.10 4.10 22 100.01 57.50 4.74 0 Charging 11010000
9130 2021-11-15 16:27:36 4.10 4.10 4.10 22 100.02 57.51 4.31 0 Charging 11010000
9131 2021-11-15 16:28:36 4.09 4.10 4.10 22 100.01 57.43 -28.46 0 Discharging 11010000
9132 2021-11-15 16:29:36 4.09 4.10 4.09 22 99.99 57.43 -20.13 0 Discharging 11010000
9133 2021-11-15 16:30:36 4.09 4.10 4.10 22 100.00 57.46 -14.05 0 Discharging 11010000
9134 2021-11-15 16:31:36 4.09 4.10 4.09 22 99.97 57.44 -12.29 0 Discharging 11010000
9135 2021-11-15 16:32:36 4.09 4.10 4.09 22 99.95 57.44 -13.54 0 Discharging 11010000
9136 2021-11-15 16:33:36 4.09 4.10 4.09 22 99.93 57.44 -6.67 0 Discharging 11010000
9137 2021-11-15 16:34:36 4.09 4.10 4.09 22 99.92 57.45 -2.95 0 Discharging 11010000
9138 2021-11-15 16:35:36 4.10 4.11 4.10 22 99.99 0.00 0.00 2 CriticalPending 11010000
9139 2021-11-15 16:36:37 4.10 4.10 4.10 22 99.99 57.50 -0.24 0 CriticalOffline 00110000
9140 2021-11-15 16:37:37 4.09 4.10 4.10 22 99.99 57.48 -0.31 0 CriticalOffline 01010000
9141 2021-11-15 16:38:37 4.09 4.10 4.10 22 99.99 57.48 -0.26 0 Discharging 11010000
9142 2021-11-15 16:39:37 4.10 4.10 4.10 22 99.99 57.48 -0.26 0 Discharging 11010000
9143 2021-11-15 16:40:37 4.10 4.10 4.10 22 99.99 57.48 -0.18 0 Idle 11010000
9144 2021-11-15 16:41:37 4.10 4.10 4.10 22 99.99 57.48 -0.18 0 Discharging 11010000
9145 2021-11-15 16:42:37 4.10 4.10 4.10 22 99.99 57.48 -0.23 0 Discharging 11010000
9146 2021-11-15 16:43:37 4.10 4.10 4.10 22 99.99 57.48 -0.24 0 Discharging 11010000
9147 2021-11-15 16:44:37 4.10 4.10 4.10 22 99.99 57.48 -0.25 0 Discharging 11010000
Looks like the voltage was zero - Thou it doesn't mention shunt time out at all. The system wasn't doing much around this time either as you can see for the few min before the event the most load was 28.46amps.
slimf
I just reread this...
I had been resetting the SOC to 100% and perhaps as the charging was still going (albeit slowly) the SOC did creep up to 100.5 etc - Thou this shouldn't cause it to start reporting 0% and trigger a critical error?
It's a clue as to what might be happening thou. I have a ticket with Batrium and hopefully, they will reply soon.
The SoC on my Batrium & Victron shunts gets over 100% too & resets itself to 100% as a "recalibration" of the Coulomb tracking (seems to happen most half decent charging days).
slimf
I got no issue with that. I have an issue with a critical fault being thrown ( and hence pack being taken offline via shunt trip) and can’t identify why.
slimf
The problems are now getting worse! I woke up this morning to discover three cells at 4.1 and the rest a 4.0 - a huge difference. After measuring the voltages at the terminals on the WM5, there is no imbalance in my cells. It looks like three cells are 'stuck' reading at 4.1v.
I didn't get a screenshot this morning before a stack of charge went into the cells, but this one shows .05 of a volt difference - the three cells circled seem 'stuck' at 4.1v (they are not at this voltage - The measured voltage is 4.05 like all the other cells.
I will try a factory reset of the thing to see if it helps. At least my heart is beating again after checking the cell voltages myself.
slimf
I performed a 'reboot' using the Reboot System function in the Hardware -> System tab and after reboot, the three stuck cells are now reporting correctly.
intra
Wow, its been a while since i've logged in and i'm now reading this thread with much interest (since i have a WM5).
Could this be related to the newer firmware that you have loaded?
Can you even downgrade?
slimf
Yeah, It's possible to downgrade the firmware - However, I have not done this.
Batrium phone support basically said to pay for support and hung up.
They later emailed me and again pushed the paid support - Which I can understand - They would get a lot of beginners trying stuff and not understanding how the system works - HOWEVER it would help if the documentation and User Interface were even moderately user friendly. The support staff also seem to use terminology that is inconsistent with the labels in the UI - Making it super hard to understand what they are trying to say.
Melanie mentioned two settings (in quotes)
1. "Charging Bypass level"
2. "charging cell volt resume"
Neither of the above two settings exist that I can find.
I could find:
'Bypass Volt'
'Cell hi resume'
Which I *THINK* Melanie is referring to, but after seeking clarification I was advised that I really should pay for an education session. The least they could do is be consistent with labelling.
They keep claiming that my time out (and ultimately the shunt tripping) is caused by shunt recalibration - But the logs I have pasted above don't really show any of that - Even the raw logs make it super hard to work out what happened. It should be bleedingly obvious, but it's not.
Anyway, I am considering paying for support to try and work it out.
The Stuck voltage reading issue isn't something they have addressed. Other users in forums and Facebook groups have had similar issues and have also failed to get any kind of reason for it. I also questioned them on the WM5 - this was a 'new' product that appears to have been discontinued quickly (according to the site it's still in beta, but it's no longer available - that in itself tells a story) - I feel I have paid for an expensive paperweight.
It's a shame about the slow releases and the terrible state of the documentation and the confusing UI. There is a real market for good quality BMS's and if they nailed it they would do really well.
slimf
Here is a screenshot from Victron's VRM - They graph the reported cell voltages as reported by Batrium. As you can see at around 2:30pm yesterday something went really wrong in the BMS and it started reporting a large change between Min/Max cell voltages. At around midday, I rebooted the BMS and the voltage measurements came good. There is no configuration setting I could have screwed up to cause phantom voltages, nor was it wiring (which remains untouched for nearly a year). Purely a software glitch solved by a reboot. Maybe it runs Windows :p
Edit: Now that I look at this, the 'Max' voltage issue could have started prior to 2:30 as the issue wasnt with the blue line, it was with the orange.
HughF
Probably a shunt timeout. I disabled shunt monitoring on mine as I had a few fault critical trips.
I only monitor cell max and min and ignore everything else.
