junction box

newone972

New member
Joined
Nov 26, 2018
Messages
18
there is my PV jucntion box4 IN + 1 out

for

8 Panels (2 in // and 4 in sries). PV = 12

4 breakers 10 A+ 2 poles switch 63A

it will be upgraded later (fuse + lignhting protection)

It's not perfect for the moment :shy:


image_xdotpi.jpg


image_mcszvd.jpg


image_youkmx.jpg
 
Don't forget the "4 hole grommets" in the cable glands for outdoor use :)
 
You're using breakers rated for AC220V only, not for DC. :exclamation: This is likely dangerous :exclamation: . DC will create an electric arc when disconnecting, and will melt/burn breakers not designed to extinguish this arc. I strongly recommend you change all breakers.
Note that DC breakers often have a +/- as well asIN(PV)/OUT(Charger) directions you have to follow.
 
Good work. Except for the ac breakers. You can get Schneider cheap on ebay made for DC :)
 