Hi guys, would be good to get some thoughts from the group on this earthing situation, probably not uncommon.
I have chatted to several electricians and got several different answers lol (no surprises)
My setup (not finished yet)
Currently, there is not going to be feedback to the house, and the setup is just for the shed to run freezers and servers.
But later down the track, I might get an electrician to feedback to the house breakout box (I have a second conduit in place if I choose to go this route)
Now with regards to earthing, one electrician said I can earth the inverter and shed breaker box on the same earth pike as the shed and the panels.
Second electrician said I should have a second earthing pike for the inverter and shed breakout box, for additional equipment protection incase of a lighting strike.
Now from my early days as an apprentice 18 years ago (before I moved on to other things and pulled the pin lol), I remember that sometimes multiple earthing can cause issues, and for closely connected wiring you should share the same earth pike as several can cause a loop impedance.
So it brings to question when I connect up the house to the PIP, later on, I should probably run an earth back to the house earth.
What have others done in this situation? the goal is safety over everything, human then equipment.
I have chatted to several electricians and got several different answers lol (no surprises)
My setup (not finished yet)
- House with full main electricity, standard breaker box with earthing.
- Shed, steel-framedon slab(1.5m from the house)
- Shed has mains feed from house supplying PIP-5048MK as backup.
- 3kw of 250w panels, in 4p3s config for 33A 92V of supply.
- Panels are earthedto the roof (and steel studs) then to anearth peg.
Currently, there is not going to be feedback to the house, and the setup is just for the shed to run freezers and servers.
But later down the track, I might get an electrician to feedback to the house breakout box (I have a second conduit in place if I choose to go this route)
Now with regards to earthing, one electrician said I can earth the inverter and shed breaker box on the same earth pike as the shed and the panels.
Second electrician said I should have a second earthing pike for the inverter and shed breakout box, for additional equipment protection incase of a lighting strike.
Now from my early days as an apprentice 18 years ago (before I moved on to other things and pulled the pin lol), I remember that sometimes multiple earthing can cause issues, and for closely connected wiring you should share the same earth pike as several can cause a loop impedance.
So it brings to question when I connect up the house to the PIP, later on, I should probably run an earth back to the house earth.
What have others done in this situation? the goal is safety over everything, human then equipment.