How hot is too hot for PV array wire?

OffGridInTheCity

Moderator
Joined
Dec 15, 2018
Messages
2,687
Hey All

I have 70feet of "6 AWG, Type MTW/UL1283 Wire, 266 Strand, Temp 105C"wire between PV array and Controller. The wire is in EMT conduit.Today - at 38a the wire is running40C/105F- e.g.'warm to the touch' and its not a problem... BUT...

How hot is too hot?

I asked because Iadded panels to max out my Midnite Classic 150s and as summer approaches they will reach 45+ amps and thehe wire will get hotter. Here's the specs:

image_bcjcni.jpg


The Midnite offers current limiting, so I can control this but I'm thinking that it will become a question of how hot is too hot (unless I run 4awg wire - a big pain!!)
 
I am using 40ft of 10 gauge supplying 99v max 19amps.. and another 19amps 99v on another set of 10 gauge then combined inside the house the a short 3ft run of wires (4 gauge) going to inverter so thats like 40 amps 99v,, they dont get warm at all.. with prior configuration I had 27amps on the same gauge wire and it got slightly warm.. Id think 6 gauge at 70ft would be thick enough to not catch fire and not have much amperage loss from heat
 
What voltage is your panels running at? Also, how many amps are you pulling?

Maybe you could bump the voltage up a little to reduce amp draw(?)
 
Maybe "Temp 105C" is maximum the cable can withstand ;-)
My conservative gut feeling would be: ~60C perfectly safe, ~75C concerning but safe

Make sure you don't have weak/hot spots in, eg connectors.

Some suggestions:
Split the array into 3p3s and 3p2s, and run another set of cables.
Replace with thicker cable.
Upgrade to Midnite Classic 250 and reconfigure array to 3p5s.
Limit charge current. <- cheapest and easiest. You won't lose much energy as the panels will rarely put out 100% anyway. Besides, on those super sunny days you'll likely get more energy than you need.
 
ajw22 said:
Make sure you don't have weak/hot spots in, eg connectors.

I agree. This could be an issue here. Perhaps there's a loose connection somewhere loosing voltage making the amps jump up higher than the installation was rated at.
 
Cables heat from the amps (current) flowing - which leads to a current carrying "ampacity" rating.
They are rated for a certain current in open air & need to be derated when enclosed in conduit or bundled with other wires, etc.
You also need to derate more again if cable/conduit is in the sun &/or temps are elevated. EMT conduit (metal) seems to get quite hot in the sun...
See here: https://www.copper.org/applications/electrical/building/pdf/a6124.pdf (there's a temp rise table in there).

This doc has cable ampacity numbers for temps to 90C rated insulation (6AWG is 75A at ambient 30C),
https://www.usawire-cable.com/pdfs/NEC AMPACITIES.pdf
This one has in conduit & 105c cable for <50V marine:
https://www.bluesea.com/resources/529/Allowable_Amperage_in_Conductors_-_Wire_Sizing_Chart
Looks like your 105C cable is rated for max 84A in conduit but you have to derate again for in sun/temp.
I couldn't find a clear temp derating number, & it varies with height off a roof surface & colour!
Say "EMT on roof" temp rise = 30C, you'd use the 75C numbers in the usawire table so that's 65A on a 30C ambient day.

So probably going to be OK with your predicted 45A in EMT conduit on a sunny day... but that cable's going to be running pretty hot.
Maybe run a parallel 6AWG pair in a separate conduit?
 
Thank you all for the comments. I have an access box where I can check temps - here's a picture of that:

image_koqsgw.jpg


@Korishan ...
>What voltage is your panels running at? Also, how many amps are you pulling?
The Midnite Classic sizing tool predicts 93.9v and I observe that is mostly 97'ish volts but can occasionally go a bit lower. So 4275w/90v = 47.5a at low end and 97v = 44a at hither voltage. But as you knowMPPT varies thru the day.

>Maybe you could bump the voltage up a little to reduce amp draw(?)
Yes, my fall back plan is to use Midnite Classic current limiter. You can limit current going to the batteries and then it will automatically limit incoming PV current because it has to be <= the current going out. I'm currently running with80a (limiter setting/circuit breaks) for the battery charging. This would be in range of80a*52v = 4160watts/95v = 44a from PV.

So all settings point to 45 +/- amps on a regular basis.

@ajw22....
>My conservative gut feeling would be: ~60C perfectly safe, ~75C concerning but safe
Yes I'm thinking that also but I appreciate the comment. I have a temp gun and willmeasure/monitor the temp as summer arrives. This temp roughly coincides with 'too hot to hold onto with fingers'

>Make sure you don't have weak/hot spots in, eg connectors.
No hot spots - just unbroken wire directly to the Midnite Classic input lugs.

>Some suggestions:
Thank you for helpful suggestions. I can limit current temporarily if I need to and thenrewire. Perhaps combine some of thecurrent wiring - use 2x6awg combined instead of 1 wire+ run some new 4AWG. Its only 70feet and is accessibleand doable - just a pain to do conduit etc.

@Redpacket... appreciate the info.
Its EMT conduit under the house where multiple strings combine to make the full 15panels (3s5p) power from the combiner box directly to the controller - 70feet of full 3s5p. The one conduit has 4 x 6AWG wires and the other has only 2 x 6AWG wires. If the temps stay within 50C/140F'ish range in the 4 x 6AWG wire run then I think it will be good but we'll see.


I'll monitor and report back on this.
 
OffGridInTheCity said:
I have 70feet of "6 AWG, Type MTW/UL1283 Wire, 266 Strand, Temp 105C"wire between PV array and Controller. The wire is in EMT conduit.Today - at 38a the wire is running40C/105F- e.g.'warm to the touch' and its not a problem... BUT...

OffGridInTheCity said:
@Korishan ...
>What voltage is your panels running at? Also, how many amps are you pulling?
The Midnite Classic sizing tool predicts 93.9v and I observe that is mostly 97'ish volts but can occasionally go a bit lower. So 4275w/90v = 47.5a at low end and 97v = 44a at hither voltage. But as you knowMPPT varies thru the day.


Ok, so 70 Feet of 6 AWG pulling around 40A. According to this chart you are exceeding the limits:

image_vkxdtq.jpg


You should be using close to 4 AWG or lower your amps. 2 AWG would be better for that distance.
 
image_meyyfa.jpg
Offgrid..I mispoke above, I separated my array into 2 sets of wires 40, each set is right at 20amps 100v (like 1830 w each) then combined (in parallel) inside the house. then its 40 amps 100v short run 3660w (3ft) of 4 gauge directly to outback charger.. going into that distribution block in the pic is 4 wires (2 positives and 2 negatives) 10 gauge (2 from each array) then 2 wires 4 gauge going to charge controller.. and like i said they barely get warm
 
Korishan said:
Ok, so 70 Feet of 6 AWG pulling around 40A. According to this chart you are exceeding the limits:

image_vkxdtq.jpg


You should be using close to 4 AWG or lower your amps. 2 AWG would be better for that distance.
Yea, but the charts don't capture all the variables. I see on others that I'm on the line due to distancebetween 6AWG and 4AWG as I go from 38amps to 48amps. Its also a matter of power loss (as apposed to danger) in some of the charts - e.g. they lead you to believe you could lose 10% of the power. I actually haven't found power loss to be so dramatic at these distances... but I'm definitely NOT an electrian.

Its really quite startling how the distance affects things. For example, I had a 1" 4AWG from bussbar to Shunt in my control box when I first turned on the additional 21 panels and the resulted in a few cases of nearly 200a flowing thru it!! and it barely got warm. I upgraded to 4/0 for that as I couldn't reconcile that in my mind and in theory it can to to 240a at full bore as summer approaches.

Its 4AWG wire from Midnite Classic to Battery - about 8 feet - with 80a on each one and they are at the 101F temp. 80a!! So distance really matters.

The 6awg wire was installed by a certified Electrician when I did the original system aswas supposed to support 50amps. But you know, I'm OK to 'question authority' as its my house / safety :)

-------
40amps at 105F seems OK to me... but regardless of Electrician I don't want'too hot to touch' (e.g. 150F'ish degrees)as it just doesn't sound like common sense. If it stays at 120F or something like that then I think I can sleep OK :) IF not, I'll combine the 2 x 6AWG to get 3AWG and run a new 4AWG line.

@Doin It - Thanks for the clarification/info!
 
When in doubt, go larger gauge wire ;) Bigger is always safer, in this instance
 
Korishan said:
When in doubt, go larger gauge wire ;) Bigger is always safer, in this instance
A light bulb clicked on in my dim brain... and I remembered thatI have unused Midnite Classic temp probes (since Batrium does the battery temps)so I've place a couple of them on the wiring inside the access boxs. I have modbus access tothe Classic data so I canmonitor/record the amps vs temp and will see what happens as spring approaches - and I can report back with some actual data/graphs :)

FYI - I do appreciate your comments - don't want you to think I'm ignoring them. I think I just want to see temps before jumping. If it stays under 50C/122F then I don't think I'll be 'that worried'. If it goes over that then....
 
Taking steps to monitor the temps is a good one. Maybe you'll find that it only gets warm at certain times and for short periods.
 
quote from ajw22:
My conservative gut feeling would be: ~60C perfectly safe, ~75C concerning but safe
quote from korishan:
When in doubt, go larger gauge wire Wink Bigger is always safer, in this instance

Both have a plus one from me.
You have one roof, what do you care about those extra amps if you can lower your charge at sunny days?
You won't even have use or storage for them, please go and be safe.

40c is nice and friendly to touch...50 you can hold, 60 is uncomfortable....
70 to touch:...your nerves will warn you, you can hold it, but...
80 is not comfortably on touch.
110c dry you can touch and grab for short period, but dry (old) wood can catch fire! at 110c
I can give you samples enough about dry wood smoldering at 80!!!!Celcius.
6 hours is to long, 4 hours can be safe.
Gut (proved) feeling and experience
Heat is building up in the wood, it will go slowly to ?chare? black bbq cole

Side note: my roof is built in 1886, old and dry, average sunny summer day, 12 hours of sun?
Go bigger on cables and lower your amps, increase volt: drop temp.

My two cents
 
@100kwh-hunter - thanks for the comments.

I've placed Midnite Classictemp sensors at 3 different wire locationsand I'm starting to get data. The ambient is 13C/55F. Here's my web monitor and I've circled the related power / wire temps by color.

RED - 3/4" EMT with 4 x 6AWG wires. Each pair carries 1 set of3s5p 285w panels for 4275w maximum. That's 4275 * 2 = 8550w in 1 conduit.
GREEN - 3/4" EMT with 2 x 6AWG wires. 1 pair of 3s5p 285w panels for 4275w maximum in its own conduit.
BLUE - Control Box where 3 x 4AWG wires tie into negative bus for battery. This is the Classic 150's output to the battery - 61a+65a+62a = 188a right now with 80a/controller = 240a max.
image_ppnkea.jpg


Today is highest yet - RED Classic #1 + #2 are getting 3369/46.1a + 3601/43.9a yielding 46.1C within the 3/4 EMT.

Notice the 'low' MPPT voltages causing high amps (46.1a + 43.9a). Maybe sunny and cool (60F outside) is causing this. MPPT voltage should bein 90s - e.g.90-97v as summer approaches - which means the amps shouldn't get much higher than they are today.
 
Based on your factors:
- the measurements you made (best indicator!)
- your 105C rated cable
- NEC code tables for your cable
- the conduit is metal not plastic
- the cable run part with about 45 amps is not in the sun or in the (hot) roof cavity it's underfloor
- the conduit run is not enclosed in insulation
you're going to be fine & you seem to have a good margin before limits or dangerous conditions
 
Gathered some more data on 12.8kw PV array. Its spring so I'm routinely getting 50+kwh and 10kw peaks.

EMT1: = combined amps of the 2 sets of 6awgwire in EMT conduit #1.
Wire = highest deg C of the wire in EMT conduit #1.

image_gywqwv.jpg


Looks like its holding <= 50C/122F so far. So its not an emergency. We'll see what summer brings.....
 
The temps have continued upward to 55C, 56C, 57C and its still spring so I rewired things today!

I took the 4 x 6 AWG wires in the original 3/4 EMT conduit and paired them up... this give an effective wire size of 3AWG and reduces the total amps inside the conduit to 50a.

Then I ran a new pair of 6 AWG in a new 3/4 EMT conduit alongside the original.

What I've learned is that running 4 x 6 AWG inside a single 3/4 EMT conduit at 50a per pair (100a total) is too much heat. A single pair of 6 AWG it's own 3/4 conduit tops out at 40C (so far) instead of 56C carrying the 50a.

Note: We're talking a 60ft run of EMT under the house with ambient temp of 15C - 25C.
 
You would think the metal EMT would keep the wire cool. Altho, I suppose it does under the house. But once you get above ground and away from the heatsink (of the earth) it heats back up.

I'll have to keep this in mind when I set mine up. Thanks for doing the leg work for us ;)
 