(05-21-2020, 11:22 PM)w0ss Wrote: I never measured the wire so I can't say for sure. 2amp might be ok but I don't want to say yes and have it break something.

Maybe I should isolate the Lifepo4 and do another test.

I see the balance leads on the module are 24 AWG.  Your resettable fuses are what amperage, and how did you select that?

That would be very interesting if you can isolate the LG for capacity test  Smile

Thanks
Reply
#62
According to wikipedia 24awg can handle 2.1amps. I picked fuses that trip @ 1.5Amps. I just made a guess... sounds like my guess was close enough Smile
Sojourner likes this post
Reply
#63
(05-21-2020, 11:22 PM)w0ss Wrote: I never measured the wire so I can't say for sure. 2amp might be ok but I don't want to say yes and have it break something.

Here are a few closeups with a penny for scale.


My test earlier in the thread showed the following.

Discharge test of the bank from 4.08(3.57) to 3.40(2.98) volts per cell was ~425AH. Nominal is 550ah(378 LiPo/172ah LifePO4).

So I had ~78% capacity from 4.08 to 3.40. Since I had the LifePO4 pack in as well not sure how mush capacity it really has. I was also discharging it at probably .05c. Maybe I should isolate the Lifepo4 and do another test.
Thanks,
Will


Awesome! thanks for the photos. That helps.  Keep us posted if you try another capacity test.
Reply
#64
I did a capacity test on just the 2 LG batteries I have. Went from 4.15v to 3.22v and had 91.5%(173AH) Cell voltages stayed pretty close until fairly low. I published a graph showing delta from min to max cell. The spike at the end is when I rebooted everything to try and fix some weirdness with my inverter. https://snapshot.raintank.io/dashboard/s...panelId=19
Sojourner likes this post
Reply
#65
(05-24-2020, 12:48 PM)w0ss Wrote: I did a capacity test on just the 2 LG batteries I have. Went from 4.15v to 3.22v and had 91.5%(173AH)

91.5%...sounds promising for the unit I got.  Although one of my cells may potentially be problematic (not dead, but giving a low voltage reading).  Still studying it...awaiting some testing/charge/discharge devices.

Is your capacity result for one of your 2 batteries?  an average?
Reply
#66
Both batteries were in parallel. I pulled out 345.338AH from the pair. Here is the Batrium screen showing the cells. They were still pretty even.
Keep in mind the 189AH rating is from 4.2 to 3.0 since I only went from 4.15 to 3.22 I left some capacity unused.

Sojourner likes this post
Reply
#67
(05-24-2020, 05:37 PM)w0ss Wrote: Keep in mind the 189AH rating is from 4.2 to 3.0 since I only went from 4.15 to 3.22 I left some capacity unused.

You're probably close to full rated capacity.  Nice  Smile