2424LV MSD How many panels in series
#1
How many panels in series can a 2424LV MSD handle if the panels have these specs.

Rated Power: 265W
Open circuit voltage (VOC): 44.20 V
Max power voltage (VMP): 35.33 V
Short circuit current (ISC): 8.20 A
Max power current: 7.50 A
Power Tolerance 0/+3%
Maximum system voltage: 600V (UL)
Fuse Rating: 15 A

The 2424lv has these specs

INVERTER MODEL 3KVA with MPPT
Rated Power 2000W
Max. efficiency 98%
Max. PV Array Open Voltage 145Vdc
Operating Voltage Range N/A
PV Array MPPT Voltage Range 30~80Vdc
Min. battery voltage for PV charge 17Vdc
Standby Power Consumption 2W
Battery Voltage Accuracy +/-0.3%
PV Voltage Accuracy +/-2V
Charging Algorithm 3-Step
Reply
#2
For those panels you would be able to 3 in series 44.2V *3 => 145V
******Hi My name is Jason and I have SOCD (Solar Obsessive Compulsive Disorder)*******
Current Powerwall - 1400 Cells 7s200p (modular 40p packs) ~ 12kWh of storage     4x 315W Canadian Solar Panels

Working on the next 7s40p packs     ~2.5kWh

Waiting on 2000 Cells of unused Sony vt4 (2000mah 30A) ~ 15kWh      hehehehehe  More Power
Reply
#3
Thank you that sounds great
Reply
#4
I'm thinking 2 in series would be safest. You're going to see more than 145Voc on a cold day from 3 in series. Of course, we don't know where he's living, so many that point is irrelevant. Although the optimal MPPT range of that charger is 30-80V and 3 in series will produce 106Vmp.

Stick with 2 in series...
Reply
#5
(03-26-2020, 06:03 PM)mike Wrote: I'm thinking 2 in series would be safest. You're going to see more than 145Voc on a cold day from 3 in series. Of course, we don't know where he's living, so many that point is irrelevant. Although the optimal MPPT range of that charger is 30-80V and 3 in series will produce 106Vmp.

Stick with 2 in series...
They have a hybrid the LV2424 that does 115v
I live in Indiana and it will sometimes get to 0 degrees Fahrenheit in the winter. Could I switch to this unit. The only problem is I can't back feed the grid. I would have to figure out if I could remove that setting.
Reply
#6
The Open circuit voltage (VOC) printed on the panel is typically for when it's 20~25degC. At 0degF, if the sky is clear and the panel is properly angled towards the sun, VOC on a typical panel could be +15% higher. Your PV panel manufacturer spec sheet should list how exactly Voc changes vs temperature.

So under perfectly bad conditions, 3 panels in series could have a Voc of 44.20 x 3 x 115% = 152.49V, which probably will not kill the inverter outright, but will likely shorten its lifespan.

Seems like 2 panels in series produces voltages that are smack in the middle of the acceptable range, which probably means highest efficiency and lifespan.
mike likes this post
Modular PowerShelf using 3D printed packs.  50kWh and growing.
https://secondlifestorage.com/showthread.php?tid=6458