Batrium Watchmon5 question
#1
I am having an odd issue and I am trying to figure it out. When the WM5 goes into bypass some of the cells will read very high for a second or two. Jumping from 4.10 to 4.2 or 4.3 I don't understand how this could happen. If anything I would expect the voltage to drop as it is bypassing .5 amps. a 189ah cell is obviously not going up and down 2/10's of a volt in a second unless it was on fire, I would ignore it as a faulty reading but it is causing my inverter to go into protect mode as the Batrium is sending it the alarm.
 
Any thoughts or has anyone seen this?
Thanks,
Will
Reply
#2
Contact batrium.
The Ultimate DIY Solar and build place
YouTube / Forum system setup / My webpage  Diy Tech & Repairs

Current: 10kW Mpp Hybrid | 4kW PIP4048 | 2x PCM60x | 100kWh LiFePo4 | 20kWh 14s 18650 |  66*260W Poly | ABB S3 and S5 Trip breakers
Upcoming: 14S 18650~30kWh
Reply
#3
I had this problem when I connected the cellmons to wire lead extensions connected to the cells instead of batriums requirement of being directly connected to the cell. I think the extra wire resistance throws the cell voltage calculation off. I ended up connecting much larger guage lead wire than the provided leads will accommodate, I think it was 10 awg wire for extending the wire. After increasing the wire size of the extension, voltage readings of adjacent cells to the cell in bypass are now accurate and they don't also go into bypass because of incorrect higher voltage.

Hope this helps.
Reply
#4
That generally only lower the voltage and doesnt raise it but its a valid sugestion.

If you dont use original wiring and length you dont have any support from Batrium in terms of error. So that need to be considered. The longmons have an impedance matching in the leads.
w0ss likes this post
The Ultimate DIY Solar and build place
YouTube / Forum system setup / My webpage  Diy Tech & Repairs

Current: 10kW Mpp Hybrid | 4kW PIP4048 | 2x PCM60x | 100kWh LiFePo4 | 20kWh 14s 18650 |  66*260W Poly | ABB S3 and S5 Trip breakers
Upcoming: 14S 18650~30kWh
Reply
#5
I will try Batrium again. I agree if it was an issue with wiring voltage should go low not high but perhaps there is something else going on.
Reply
#6
Have you fiddled with the wires at all?
The Ultimate DIY Solar and build place
YouTube / Forum system setup / My webpage  Diy Tech & Repairs

Current: 10kW Mpp Hybrid | 4kW PIP4048 | 2x PCM60x | 100kWh LiFePo4 | 20kWh 14s 18650 |  66*260W Poly | ABB S3 and S5 Trip breakers
Upcoming: 14S 18650~30kWh
Reply
#7
I also agree that the voltage would appear to go down with the current draw from the cellmons, but for some reason, it caused my adjacent cellmons to rise in voltage only when in bypass.
Reply
#8
Daromer, yeah i have redone the cabling a few times and the issue persists. not saying it isnt the cabling but still investigating.

Tentious, Interesting as this is on a Watchmon5 which is designed to work on shared wiring looms.
Reply
#9
w0ss, you're correct, I have watchmon 4, so I guess my comments are not valid as long as the balance lead wires are within spec(length and gauge). I'd also contact Batrium for support, they are generally pretty quick to respond.
Reply
#10
Ah yeah wm5 and 4 works differently in how they meassure. WM5 meassure every 2nd at a time with integrated chipset. It sounds weird it raises but i have not used the 5 enough to say anyting more than Batrium have showed.
The Ultimate DIY Solar and build place
YouTube / Forum system setup / My webpage  Diy Tech & Repairs

Current: 10kW Mpp Hybrid | 4kW PIP4048 | 2x PCM60x | 100kWh LiFePo4 | 20kWh 14s 18650 |  66*260W Poly | ABB S3 and S5 Trip breakers
Upcoming: 14S 18650~30kWh
Reply