Hi DIYers,
I have a message into Schneider about this issue, but have yet to receive a response. Wondering if anyone here might have an answer.
I have a 6848 XW+ connected to 14S7P Leaf module battery. I have Grid Support enabled and the Grid Support & Recharge voltage setting at 50 volts so that when battery gets down to that level it's supposed to go into charge mode. Inverter goes into AC Pass Through 0.5 volts above this setting and only a few watts is drawn from battery at this point thus it would take days for it to reach the 50 volt level. I have to manually change the Recharge setting to 50.5 volts to get charge cycle to start. On a seemingly related setting:
Grid Voltage Support is nowhere to be found in the manual. Not sure what this is supposed to do. I have tried several other tweaks involving load shed and sell to grid with no resolution. Any ideas on these issues would be appreciated. Thanks
I have a message into Schneider about this issue, but have yet to receive a response. Wondering if anyone here might have an answer.
I have a 6848 XW+ connected to 14S7P Leaf module battery. I have Grid Support enabled and the Grid Support & Recharge voltage setting at 50 volts so that when battery gets down to that level it's supposed to go into charge mode. Inverter goes into AC Pass Through 0.5 volts above this setting and only a few watts is drawn from battery at this point thus it would take days for it to reach the 50 volt level. I have to manually change the Recharge setting to 50.5 volts to get charge cycle to start. On a seemingly related setting:
Grid Voltage Support is nowhere to be found in the manual. Not sure what this is supposed to do. I have tried several other tweaks involving load shed and sell to grid with no resolution. Any ideas on these issues would be appreciated. Thanks