Reading label on a circuit breaker
#1
I'm looking at a 480v(ac) 3P 30A breaker,
dual rated for 250vdc 10ka

On the label it says this:

"Use Two 100% Protected Poles for DC"

Does that mean you can only use 2 of the 3 P for DC?
Or are you supposed to use 1P for + and 1P for - (Guessing no...)
... Or something else entirely?
Reply
#2
Perhaps the manufacturer of the circuit breaker has a pdf on the 3 pole circuit breaker explaining how to use it for dc.


later floyd
Reply
#3
EHD3030L is the breaker,
I didn't find anything in their PDF's for DC,

But I did find a picture of a new breaker which has a slightly different text:

"Use (2) 100% Protected Poles In Series For DC"

Which makes (a little) more sense.
Reply
#4
Yeah, I've seen some schematics and statements where you use "2" breakers in series for DC. I suppose 1 will start to trigger and the 2nd one finishes(?) I don't know the theory behind it.
Proceed with caution. Knowledge is Power! Literally! Cool 
Knowledge is Power; Absolute Knowledge is Absolutely Shocking!
Certified 18650 Cell Reclamation Technician

Please come join in general chit-chat and randomness at Discord Chat (channels: general, 3d-printing, linux&coding, 18650, humor, ...)
(this chat is not directly affiliated with SecondLifeStorage; VALID email req'd)
Reply
#5
I can think of 2 possibilities,
Maybe you just need the extra effective breaking speed and distance to meet the 250v rating.
Or maybe they have magnetic arc arestors, and you put 2 in series to cover you for both current directions.
Reply
#6
I ran into a similar question for myself on two pole breakers.  

I think they mean that you need to wire it like this. I'm not saying this is correct, but I made this for discussion purposes.

[Image: TVON5dp.jpg?1]
Bilabob likes this post
Reply
#7
@Crimp Daddy - What would be the logic of doing something like in the picture's left ?
Reply
#8
Higher voltage tollerance. Larger gap basically.
Crimp Daddy likes this post
The Ultimate DIY Solar and build place
YouTube / Forum system setup / My webpage  Diy Tech & Repairs

Current: 10kW Mpp Hybrid | 4kW PIP4048 | 2x PCM60x | 100kWh LiFePo4 | 20kWh 14s 18650 |  66*260W Poly | ABB S3 and S5 Trip breakers
Upcoming: 14S 18650~30kWh
Reply
#9
(07-28-2020, 08:32 AM)Overmind Wrote: @Crimp Daddy - What would be the logic of doing something like in the picture's left ?

Generally speaking... and depending on the breaker, I have seen an increase in capability/rating when doing this.

Depending on the system voltage and requirements, it may be necessary to wire it in this manner.

As an example, here is the side of my ABB.  Max voltage is different for 2 pole and 3 pole wiring.


[Image: sFhGYwt.png]
OffGridInTheCity likes this post
Reply
#10
Interesting, I never imagined such an use before seeing this.
Reply