newbie question about amps/loads
#1
Hi,

I'm new to DIY powerwalls and wiring. If I have 2 24 volt batteries in parallel and my inverter pulls a 20 amp load, does this get split 10 amps to each bank?
Reply
#2
Yes, pretty much.
If the batteries are in similar condition & similar capacity, it'll likely be pretty equal.
But if one has higher internal resistance eg because it's older or maybe much colder than the other it would be different.
Running off solar, DIY & electronics fan :-)
Reply
#3
Note also that even if they start out in similar health and roughly share the load, they typically won't remain that way as they age, so you'd need to periodically check how well-balanced they remain. Even batteries from the same batch can have highly diverging IR as they age, which can greatly disturb load balancing.
Reply
#4
Wouldn't it also matter how the batteries are connected to the load?
one battery has the positive of the combined 24v battery and the other battery has the negative?
 
Later floyd
Korishan likes this post
Reply
#5
(08-12-2020, 04:01 PM)floydR Wrote: Wouldn't it also matter how the batteries are connected to the load?
one battery has the positive of the combined 24v battery and the other battery has the negative?
 
Later floyd

Yes, but generally that is more dependent on higher amp loads. However, 20A is pretty significant, even for lead acid batteries. Though, the OP doesn't mention if it's lead acid or lithium. This also makes a difference of how things will maintain balance; especially if it's 24v lithium-ion based which does not 'really' fit 24v systems, but better than 12v
Proceed with caution. Knowledge is Power! Literally! Cool 
Knowledge is Power; Absolute Knowledge is Absolutely Shocking!
Certified 18650 Cell Reclamation Technician

Please come join in general chit-chat and randomness at Discord Chat (channels: general, 3d-printing, linux&coding, 18650, humor, ...)
(this chat is not directly affiliated with SecondLifeStorage; VALID email req'd)
Reply
#6
I'm running two batteries which contain 140 (7s20p) 18650 cells each, which each batteries having a BMS system. Specifically the jehu pcbs and bms. Each bms is rated for ~50 amps but the boards specify a 40 amp limit without modification. They are connected in parallel to copper bus bars which are feed by a solar MPPT charge controller which maxes out at 80 amps.

I typically have a load connected to this system and the system will feed to thr load before the battieries, so there is almost never 80 amps avaliable to charge between load and panel output.

In theory even if it did have 80 amps of charging it should split 40 to each bank? (assuming similar health and capacity).

I'm planning to add an 3rd battery in the future for more capacity and it seems like this would further spread out the charging amps.
Reply
#7
(08-12-2020, 05:47 PM)Eddieb Wrote: [...] In theory even if it did have 80 amps of charging it should split 40 to each bank? (assuming similar health and capacity).

In theory (by Ohm's law) the current would split perfectly halved if each pack has the same total resistance, which includes both the (total) pack IR (internal resistance), along with the resistance of the cables going to each pack (try to keep them the same length/type). But it's complicated by the fact that IR depends on temperature and SOC, which may differ for each pack (they may have different IR vs SOC/temp profiles if they are a motley mix of chemistries and models).
Reply
#8
 

In this example there are 3 ways to connect batteries in parallel to loads.

As you can in the first one, the Pos and Neg main leads are connected to the same battery. This is generally considered a bad idea as due to Ohm's law, the second battery will see a higher voltage drop than battery 1. This is because the wire has resistance. The longer the run, the higher the resistance.

With option #2, Pos and Neg are on opposite ends of the parallel connections. This makes it so that current "must" flow the full length of the wire for "both" batteries. This works for 3 or more batteries as well.

With option #3, it is "kind of" a hybrid between the two. However, current "should" flow the full distance and both. However, if there is a somewhat loose connection on either battery, that will cause a slow down of flow to/from that one.

If all runs are equal, then all batteries should see the same current/resistance. In theory this is accurate. In a perfect work this is accurate. In practical application, there will always be a difference between batteries. And, with the higher the amp load, the higher the resistance and the higher the imbalance. This is partially why you should always have a heavy main buss wire to minimize resistance as much as possible.
Proceed with caution. Knowledge is Power! Literally! Cool 
Knowledge is Power; Absolute Knowledge is Absolutely Shocking!
Certified 18650 Cell Reclamation Technician

Please come join in general chit-chat and randomness at Discord Chat (channels: general, 3d-printing, linux&coding, 18650, humor, ...)
(this chat is not directly affiliated with SecondLifeStorage; VALID email req'd)
Reply
#9
^^^ For the record, the source of the above image appears to be How to: Connect two batteries in parallel, by Simon P. Barlow, on the site Caravan Chronicles  - a caravan blog. This is the number one google (image) result if you search on that title.

There is much further discussion of that topic there (which I have not read so I don't know how reliable it is).

@Korishan  Given that the author has complained there about people copying his copyrighted images without permission, it might be a good idea to get permission (or find an alternate image).
Reply
#10
This is how they are currently connected. Once my isolator mounts come in I'll tidy up the large wires.

Bus bars https://imgur.com/a/JAKYSjV